WBIO-DI-WD-14 нету в списке устройств для WB-MIO

Работает через MODBUS-RTU но не работает через ethernet WB-MIO-E

консоли куча ошибок вида:
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: device modbus_io:37:1 disconnected
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: IODIR: setup register <modbus_io:37:1:: 10000> <-- 65535
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: WARNING: device ‘modbus_io:37:1’ register ‘<modbus_io:37:1:: 10000>’ setup failed: Serial protocol error: failed to write @ 10000: Serial protocol error: invalid crc
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: device modbus_io:37:1 disconnected
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: ModbusRTU::ReadRegisterRange(): failed to read 2 holding(s) @ 6 of device modbus:25: Serial protocol error: malformed response: invalid data size
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: IODIR: setup register <modbus_io:37:1:: 10000> <-- 65535
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: IPOL: setup register <modbus_io:37:1:: 10001> <-- 0
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: WARNING: device ‘modbus_io:37:1’ register ‘<modbus_io:37:1:: 10001>’ setup failed: Serial protocol error: failed to write @ 10001: Serial protocol error: request and response slave id mismatch
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: GPINTEN: setup register <modbus_io:37:1:: 10002> <-- 65535
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: WARNING: device ‘modbus_io:37:1’ register ‘<modbus_io:37:1:: 10002>’ setup failed: Serial protocol error: failed to write @ 10002: Serial protocol error: invalid crc
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: DEFVAL: setup register <modbus_io:37:1:: 10003> <-- 0
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: INTCON: setup register <modbus_io:37:1:: 10004> <-- 0
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: ModbusRTU::ReadRegisterRange(): failed to read 1 holding(s) @ 8 of device modbus:176: Serial protocol error: malformed response: invalid data size
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: ModbusRTU::ReadRegisterRange(): failed to read 2 holding(s) @ 97 of device modbus:176: Serial protocol error: invalid crc
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: WARNING: device ‘modbus_io:37:1’ register ‘<modbus_io:37:1:: 10004>’ setup failed: Serial protocol error: failed to write @ 10004: Serial protocol error: invalid crc
Jun 25 16:05:56 wirenboard-ALXPHKOD user.notice serial: Init: IOCON: setup register <modbus_io:37:1:: 10005> <-- 17476
Jun 25 16:05:57 wirenboard-ALXPHKOD user.notice serial: ModbusRTU::ReadRegisterRange(): failed to read 2 holding(s) @ 270 of device modbus:176: Serial protocol error: malformed response: invalid data size
Jun 25 16:05:57 wirenboard-ALXPHKOD user.notice serial: WARNING: device ‘modbus_io:37:1’ register ‘<modbus_io:37:1:: 10005>’ setup failed: Serial protocol error: failed to write @ 10005: Serial protocol error: invalid crc
Jun 25 16:05:57 wirenboard-ALXPHKOD user.notice serial: Init: CONFIG-FLAG: setup register <modbus_io:37:1:: 9999> <-- 1
Jun 25 16:05:57 wirenboard-ALXPHKOD user.notice serial: WARNING: device ‘modbus_io:37:1’ register ‘<modbus_io:37:1:: 9999>’ setup failed: Serial protocol error: failed to write @ 9999: Serial protocol error: request and response slave id mismatch

Сам MIO с контроллера пингуется? Какой адрес контроллера?

Адрес (modbus адрес) на MIO менялся?
Нет ли где-то на портах другого (возможно отключеного) устройства с таким же адресом?

в общем обнаружил что если подключено WB-MIO-E и через RS-485 и через Ethernet то независимо от настроек 485 и Ethernet он не работает. подключать надо только по одному интерфейсу, даже если второй использовать не планируется.
Добавьте, пожалуйста, это в документацию

А! Одновременно. Понятно, вот откуда проблема.
Дело в том что по сути шина 485 - она “после” Ethernet.
Но в документацию - добавил.
Сейчас работает?
Добавляю в следующую версию пакета шаблон именно под wd-14.

да, в таком варианте (неподключен RS-485 к WB-MIO-E, шаблон WBIO-DI-DR-14) работает.

Отлично. Сейчас занят оформлением вводных статей - как раз надо будет туда включить объяснения по поводу шины.