WB-MSW v3 invalid crc

Обратил внимание, что не поступают данный с датчика.
Поиск в логах по строке modbus:73 выдаёт следующее:

Самые ранние

|07-08-2024 17:28:37.288 [wb-mqtt-serial]|WARNING: [modbus] failed to read 12 input(s) @ 0 of device modbus:73: Serial protocol error: malformed response: invalid crc|
|07-08-2024 17:09:04.155 [wb-mqtt-serial]|WARNING: [modbus] failed to read 4 input(s) @ 280 of device modbus:73: Serial protocol error: malformed response: invalid crc|
|07-08-2024 17:06:25.913 [wb-mqtt-serial]|WARNING: [modbus] failed to read 2 coil(s) @ 5001 of device modbus:73: Serial protocol error: request timed out|
|07-08-2024 17:05:12.797 [wb-mqtt-serial]|WARNING: [modbus] failed to read 4 input(s) @ 280 of device modbus:73: Serial protocol error: malformed response: invalid crc|
|07-08-2024 17:03:30.731 [wb-mqtt-serial]|WARNING: [modbus] failed to read 22 input(s) @ 250 of device modbus:73: Serial protocol error: malformed response: invalid crc|
|07-08-2024 16:56:34.497 [wb-mqtt-serial]|WARNING: [modbus] failed to read 12 coil(s) @ 0 of device modbus:73: Serial protocol error: request timed out|
|07-08-2024 16:56:34.497 [wb-mqtt-serial]|WARNING: [modbus] failed to read 12 coil(s) @ 0 of device modbus:73: Serial protocol error: request timed out|
|07-08-2024 16:54:34.434 [wb-mqtt-serial]|WARNING: [modbus] failed to read 7 coil(s) @ 5100 of device modbus:73: Serial protocol error: malformed response: invalid crc|
|07-08-2024 16:39:26.029 [wb-mqtt-serial]|WARNING: [modbus] failed to read 2 coil(s) @ 5001 of device modbus:73: Serial protocol error: request timed out|
|07-08-2024 16:35:09.699 [wb-mqtt-serial]|WARNING: [modbus] failed to read 12 input(s) @ 0 of device modbus:73: Serial protocol error: request timed out|
|07-08-2024 16:35:09.699 [wb-mqtt-serial]|WARNING: [modbus] failed to read 12 input(s) @ 0 of device modbus:73: Serial protocol error: request timed out|
|07-08-2024 16:35:09.699 [wb-mqtt-serial]|WARNING: [modbus] failed to read 12 input(s) @ 0 of device modbus:73: Serial protocol error: request timed out|

Самые свежие

16-09-2024 01:09:40.015 [wb-mqtt-serial]	WARNING: [serial device] device modbus:73 is disconnected
16-09-2024 01:09:40.015 [wb-mqtt-serial]	WARNING: [modbus] failed to read 7 coil(s) @ 5100 of device modbus:73: Serial protocol error: request timed out
16-09-2024 01:09:38.847 [wb-mqtt-serial]	WARNING: [modbus] failed to read 2 coil(s) @ 5001 of device modbus:73: Serial protocol error: request timed out
16-09-2024 01:09:37.174 [wb-mqtt-serial]	WARNING: [modbus] failed to read 12 coil(s) @ 0 of device modbus:73: Serial protocol error: request timed out
16-09-2024 01:05:29.974 [wb-mqtt-serial]	WARNING: [modbus] failed to read 12 coil(s) @ 0 of device modbus:73: Serial protocol error: malformed response: invalid crc

Серийный номер 108437
Версия прошивки 4.31.6

Перед отказом никаких работ не производилось.

Добрый день!

Прикрепите, пожалуйста, диагностический архив.

Также, подскажите, как организована шина RS-485 и питание?

приложен диагностический архив, доступен только сотрудникам поддержки
(304,1 КБ)

WB-MIO-E v.2 подключен по Modbus-Ethernet.
К нему подключены WBIO-DO-R10R-4, WB-MR6C v3 и WB-MSW v3. Первые два работают.

Питание WB-MIO-E v.2 от БП TDFE
Питание WB-MSW v3 по modbus

Вскрыл крышку, там какой то индикатор моргает.

Ещё WBIO-DO-R10R-4 и WB-MR6C v3 работающие от того же WB-MIO-E v.2 сейчас реагируют с большой задержкой на изменение контролов

В архиве вижу следующее:

сен 20 13:06:45 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:08:54 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:11:03 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:13:11 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:15:19 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:17:28 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:19:36 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:21:45 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:23:54 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:26:02 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:28:10 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:30:19 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:32:32 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:34:41 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:36:49 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:38:57 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:41:04 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:43:12 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:45:19 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:47:28 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:49:38 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors
сен 20 13:51:46 wirenboard-AIAYP3DV wb-mqtt-serial[16276]: WARNING: <192.168.1.26:23>: closed due to repetitive errors

Похоже на проблемы физического подключения. Проверьте, пожалуйста, соответствие рекомендациям: RS-485:Физическое подключение — Wiren Board.

С WB-MIO-E такая проблема встречается, как правило, при отсутствии терминирующего резистора.

С августа прошлого года всё работало без проблем. Отсутствие терминирующего резистора могло проявится со временем?

Да, как и другие нарушения физического подключения.

Посмотрел физическое подключение, аномалий не выявил.

Снял датчик и подключил на modbus линию от самого контроллера, отключив исправный датчик WB-MSW v3. Результат был аналогичный closed due to repetitive errors.

Сделав заключение, что проблема не в линии, а в датчике, я вернул на место старый датчик и уже было хотел отписать сюда результаты, как началось странное.
От старого рабочего датчика начинают приходить все контролы, кроме Co2 и VOC. Через какое то время (меньше минуты) данные от Co2 появляются, а ещё через несколько секунд все контролы помечаются красным. Более того красным помечаются все контролы от реле WB-MR6LV/S, который стоит перед датчиком.

Отключив датчик от линии реле WB-MR6LV/S вернулось в штатный режим. Попытавшись подключить датчик обратно всё повторилось: Co2, VOC, задержка, отказ датчика и отказ реле.

Итого теперь у меня вышли из строя 2 датчика WB-MSW v3. Кто-то понимает, что происходит?)

приложен диагностический архив, доступен только сотрудникам поддержки
(333,2 КБ)

Посмотрите, пожалуйста, если подать на WB-MSW только питание, зелёный светодиод статуса как себя ведёт? Включается в первые две секунды подачи питания? Горит ли после?

Выше по видео вижу, что зелёный статусный светодиод не горел.

Сообщите, пожалуйста, серийные номера датчиков.


Ничего не горит ни в момент включения ни после, он вообще где, посередине?

Серийники на фото, приобретались по заказу #190073

А можете, пожалуйста, измерить напряжения на клеммах питания устройства и сделать фото с мультиметром?

Статусный светодиод - вот тут:
image

Статус моргает 2 раза и после горит. Мультиметр показывает 11.78v. Обязательно фотографировать? У меня третьей руки не хватает для фото)

Поняла, с другой стороны смотрели.

Проверьте, пожалуйста, единственным устройством на свободный порт, коротким кабелем.

Подключил первый, все контролы заработали кроме VOC. Через пару минут VOC стал в состояние ОК, но на экране устройств показывал 0.
Из строя за 5 мин не вышел.
Диод моргает.

Подключил второй, контролы красные, в логах те же ошибки, диод горит, но не моргает.
diag_AIAYP3DV_2024-09-25-14.55.56.zip (334,9 КБ)

А сканированием находится?

Это значит, что модуль почему-то не получает modbus-команд. Такое может быть из-за несовпадения параметров порта или адреса устройства.

Предлагаю просканировать шину встроенным сканером, если не найдёт, то вручную из консоли.

Есть ли возможность с кем то созвониться, чтобы в онлайн режиме я сделал всё что требуется за раз?)

Вроде же достаточно быстро переписываемся?
Сейчас уже рабочий день окончен, можем завтра в рабочее время (с 10 до 18 МСК) в том же темпе разобрать проблему?

Вроде бы просканировать вручную - это последнее, что я могу предложить. Дальше только замена.

Ну ещё на всякий случай проверить, что он не в загрузчике.

А с тем датчиком, который заработал - повесить на шину и добавить терминатор на второй конец шины (терминатор в контроллере включен по умолчанию).