Повторяются сообщения knx

Добрый день!
При просмотре шины knx
knxtool vbusmonitor1 local:/var/run/knx

L_Busmon: BC FF 7F 61 01 D1 00 81 F3 :L_Data low from 15.15.127 to 12/1/1 hops: 05 T_Data_Group A_GroupValue_Write (small) 01 
L_Busmon: BC FF 02 61 01 E1 00 81 BE :L_Data low from 15.15.2 to 12/1/1 hops: 06 T_Data_Group A_GroupValue_Write (small) 01 
L_Busmon: BC FF 7F 61 01 D1 00 80 F2 :L_Data low from 15.15.127 to 12/1/1 hops: 05 T_Data_Group A_GroupValue_Write (small) 00 
L_Busmon: BC FF 02 61 01 E1 00 80 BF :L_Data low from 15.15.2 to 12/1/1 hops: 06 T_Data_Group A_GroupValue_Write (small) 00 
L_Busmon: BC FF 7F 61 01 D1 00 81 F3 :L_Data low from 15.15.127 to 12/1/1 hops: 05 T_Data_Group A_GroupValue_Write (small) 01 
L_Busmon: BC FF 02 61 01 E1 00 81 BE :L_Data low from 15.15.2 to 12/1/1 hops: 06 T_Data_Group A_GroupValue_Write (small) 01 
L_Busmon: BC FF 7F 61 01 D1 00 80 F2 :L_Data low from 15.15.127 to 12/1/1 hops: 05 T_Data_Group A_GroupValue_Write (small) 00 
L_Busmon: BC FF 02 61 01 E1 00 80 BF :L_Data low from 15.15.2 to 12/1/1 hops: 06 T_Data_Group A_GroupValue_Write (small) 00

1 раз в 1-2 недели начинают повторятся данные сообщения без остановки (или другой групповой адрес). Управление по knx зависает, потому что сообщения не останавливаются, пока не перезагрузишь.

приложен диагностический архив, доступен только сотрудникам поддержки
(673,5 КБ)

Добрый день.
А чьи адреса (источника) указаны в логе? То есть - кто отправляет эти сообщения?

image

А 127 это hdl панель которая работает через LAN

Так, соответственно я вижу зацикливание. Очевидно что в системе есть несколько групповых адресов, телеграммы на которые вызывают отправку на 12/1/1 значений. Ну и соответственно начинается борьба. Проверьте проект - что и с чем связано?